  1. #1
    Carduelis is online now Registered User
    Location : Live in Cambridge. Boat at Woolverstone
    Join Date
    Apr 2006
    Posts
    214

    Default Webasto Air Top heating problem

    The heating system is currently only producing luke warm air. You can comfortably hold your hand in front of the vents, wheras last winter it was too hot to do so for more than a few moments.

    The heater had a full service from Deisco last year and has only done a few hours since, so I'm reluctant to believe it's coked up again.

    What I have noticed is that adjsuting the cabin thermostat seems to make very little difference although I can't remember how this is supposed to operate. When the thermostat is 'off' (i.e. up to temp) is it supposed to switch off the fan, or does it just turn down the heat inside the unit?

    What would be the best way of testing the thermostat?

    Can anyone advise please?

  2. #2
    Join Date
    Feb 2004
    Posts
    3,155

    Default

    When up to temp the fan still runs.
    Best to ring Toby at KETO he is the expert
    01202 690 900

  3. #3
    pcatterall is offline Registered User
    Location : East Lancashire
    Join Date
    Aug 2004
    Posts
    2,840

    Default

    When did it start to go wrong? Gradually or all at once? Had you moved/changed anything? Does it run hot after start up then slow down? Does it smoke?
    This can occur when the heater uses its internal thermostat and the outlet is near the inlet.... the heater is fooled into thinking it has reached the right temp.
    The fan ( as stated ) should not cycle on and off when set temp is reached, the heater should slow down and maintain required temp.
    You could by pass the thermo for a while which would make the heater run at high power ( join the Grey? wire)

  4. #4
    Join Date
    Jun 2009
    Posts
    8,046

    Default

    Quote Originally Posted by pcatterall View Post
    When did it start to go wrong? Gradually or all at once? Had you moved/changed anything? Does it run hot after start up then slow down? Does it smoke?
    This can occur when the heater uses its internal thermostat and the outlet is near the inlet.... the heater is fooled into thinking it has reached the right temp.
    The fan ( as stated ) should not cycle on and off when set temp is reached, the heater should slow down and maintain required temp.
    You could by pass the thermo for a while which would make the heater run at high power ( join the Grey? wire)
    Our Webasto Airtop (just a year old and professionally fitted) shuts down completely when the boat is up to temperature - always has. It does cut the output back a bit as it is approaching the thermostat temperature, but it certainly shuts down when significantly over temperature. I leave it switched on all winter with the thermostat set very low to protect against frost - could not do that if the fan was running continuously.

    Note that it takes a couple of minutes to cycle down once it is up to temperature - it needs to pass some cold air through the combustion chamber to bring things down to a safe temperature before cutting the fan.
    Last edited by maby; 26-11-12 at 19:37.

  5. #5
    Carduelis is online now Registered User
    Location : Live in Cambridge. Boat at Woolverstone
    Join Date
    Apr 2006
    Posts
    214

    Default

    Quote Originally Posted by pcatterall View Post
    When did it start to go wrong? Gradually or all at once? Had you moved/changed anything? Does it run hot after start up then slow down? Does it smoke?
    This can occur when the heater uses its internal thermostat and the outlet is near the inlet.... the heater is fooled into thinking it has reached the right temp.
    The fan ( as stated ) should not cycle on and off when set temp is reached, the heater should slow down and maintain required temp.
    You could by pass the thermo for a while which would make the heater run at high power ( join the Grey? wire)
    Nothing has changed, we just just haven't really used it since about last March when it was working fine. No smoke, other than a puff of buish smoke at start up. My current thinking is that the thermostat has stuck 'off' (i.e. up to temp) and so the heater is permenantly in low power mode.

    I agree that the best test is to try and bypass the thermostat. Can you explain a bit more about the "grey wire" please? Is this on the thermostat or the controller unit?

    Many thanks for your inputs BTW.

  6. #6
    Join Date
    Feb 2004
    Posts
    3,155

    Default

    Just ring Toby !

  7. #7
    pcatterall is offline Registered User
    Location : East Lancashire
    Join Date
    Aug 2004
    Posts
    2,840

    Default

    Thermostat wire. I am an eberspacher man so not sure what the webasto set up does.
    Grey is in fact the eber colour wire for the thermo. On the eber system the main switch still controls the desired heat setting and the room thermostat ( when used) just feeds into that so there are just two wires to it. I GUESS that when the temp is reached the circuit is broken and the heater shopuld slow until the circuit is 'made'' again. I cant find any diagrams showing a webasto thermostat set up here and in any case yours may be a 'one off' fitting. Sorry I cant help more.
    I am suprised that Maby's system shuts down completly at temp. This can happen in an eber when the required heating is set so low that the heater cant actually run at that temp and will then cycle on and off, but even then the fan will run for some time to prevent the heater body overheating.

  8. #8
    Join Date
    Jun 2009
    Posts
    8,046

    Default

    Quote Originally Posted by pcatterall View Post
    ...

    I am suprised that Maby's system shuts down completly at temp. This can happen in an eber when the required heating is set so low that the heater cant actually run at that temp and will then cycle on and off, but even then the fan will run for some time to prevent the heater body overheating.
    I did report that it runs the fan for several minutes after the burner has shut down to cool off the chamber. It certainly gets into cycling on and off at relatively high temperatures - around 20 degrees by the cabin thermometer.

    I must say that the Webasto control box is not the most sophisticated I've ever seen - the temperature setting on the thermometer for a given cabin temperature is a bit hit and miss. There are times when I'm feeling cold and it has not switched on and other times when we have the oven on and the boat is like a sauna, but the Webasto is still running like a jet engine.

  9. #9
    Join Date
    Sep 2001
    Posts
    1,001

    Default

    Quote Originally Posted by maby View Post
    I did report that it runs the fan for several minutes after the burner has shut down to cool off the chamber. It certainly gets into cycling on and off at relatively high temperatures - around 20 degrees by the cabin thermometer.

    I must say that the Webasto control box is not the most sophisticated I've ever seen - the temperature setting on the thermometer for a given cabin temperature is a bit hit and miss. There are times when I'm feeling cold and it has not switched on and other times when we have the oven on and the boat is like a sauna, but the Webasto is still running like a jet engine.
    Our warm air central heating at home displays the same facets. Sometimes we feel frozen and have to turn it up to get it to blow and at other times we are boiling and it is still blowing! I've come to the conclusion that humans measure temperature coupled with humidity;whilst thermostats just measure temperature!

  10. #10
    thalassa's Avatar
    thalassa is offline Registered User
    Location : +51 21' 8.64", +4 6' 39.24"
    Join Date
    Feb 2003
    Posts
    703

    Default

    Quote Originally Posted by Carduelis View Post
    The heating system is currently only producing luke warm air. You can comfortably hold your hand in front of the vents, wheras last winter it was too hot to do so for more than a few moments.

    The heater had a full service from Deisco last year and has only done a few hours since, so I'm reluctant to believe it's coked up again.

    Can anyone advise please?
    Perhaps some dust has accumulated in the cabin sensor, if it is an external one.
    It is a very simple device, a NTC thermistor, mounted in a small open cage. The contacts are quite close together, and conductive dust (salt air) can lower the resistance, and correspondingly simulate a higher temperature.
    Just measure the resistance at the contacts, it should be about 14.1 kOhms at 18 deg.C.
    Last edited by thalassa; 27-11-12 at 17:06. Reason: spelling mistakes